Requirements and installation
The additional requirements and necessary installation steps for the S7 Plus driver.
Requirements
- Installed WinCC OA version
- A valid S7Plus license (depending on the acquired license up to 8, 64 or 512 connections are available; for more information regarding calculation of connections refer to Licensing and FAQ - S7 Plus Driver).
Please note that it is NOT possible to combine two licenses, e.g. License A: 64 connections, license B: 64 connections will not provide 128 connections in total, but only the 64 connections the active license provides.
- Following S7 PLCs are supported:
- S7-1200
- S7-1500 & S7-1500R/H
- S7-1500 Software Controller
- ET200SP
You have to enable and configure "System IP addresses for switched communication" when using S7-1500R/H systems. This allows to connect to both PLCs and automatic connection switches in case one of the single connection fails. The defined system IP address must be entered as "Connection 1" in the configuration panel of the S7Plus driver.
Since no TCP connection is possible during the SYNCUP phase of the S7-1500R/H system, values are lost in this time period.
TSPP
Following additional requirements must be considered when using the "Receive Mode" TSPP:
- Only S7-1500 PLCs with a firmware version 2.6 and newer are supported.
TIA-Portal
All TIA-Portal versions >= V13.1 are supported but only the latest plugins are delivered as part of the WinCC OA installation. Older plugins can be downloaded here.
All TIA projects that shall be used by the driver must be available as a TIA export file at runtime. Therefore the projects must be exported via the TIA portal's export tool. The export tool is stored under <wincc_oa_path>/data/clsetup after installing the S7Plus component. Install the appropriate tool (V13SP1, V14 or V15). Start the TIA portal, right-click on the project or a PLC and select "Export to SIMATIC SCADA" in the context menu. The exported project must be stored under <WinCC_OA_Proj>/data/TIA_Projects on the host where the driver is running. This also applies to the redundant driver in case of a redundant project.
TIA export files larger than 128 MB cannot be used and result in the following error message: WCCOAs7plus (1), 2017.06.12 12:04:29.134, SYS,SEVERE, 54, Unexpected state, Error in decoding TIA Project <project name>, too large document
For information on supported platforms for the S7Plus driver refer to the chapter Drivers - Supported Platforms of the main Drivers.
TSL connection
Please note that a TLS connection can only be used with TIA Portal V17 and S7-1500 firmware V2.9 and S7-1200 V4.5 and later
Configuration Import Restriction
Please note, that combining the TIA Importer and Mass parameterization is not supported as it will lead to inconsistent configuration results.
Installation
For using the S7Plus driver, the menu entry "S7Plus driver" must be selected during the WinCC OA installation. In this case the Siemens S7DOS component is automatically installed. You have to restart the computer after the S7DOS installation.
The S7DOS component cannot be uninstalled.
The "Repair" option of the WinCC OA setup is not supported for the S7Plus driver. Thus, in case of a setup error of the driver or S7DOS, you have to completely uninstall and reinstall WinCC OA.
Refer to the installation chapter for further information on installing WinCC OA.