S7 - SINUMERIK

This mode allows the usage of the S7 driver to interact with devices supporting the SINUMERIK standard.

Restrictions

Following restrictions must be considered when using the "S7 - SINUMERIK" mode:

  • Redundant device/connection is not supported
  • Alarms are not supported
  • Symbolic addresses are not supported

Test Hardware

The S7- SINUMERIK interface implementation has been officially tested with following hardware and software:

  • SINUMERIK 840D SL
  • NC Operate Software 4.8 SP4 HF1
  • NC Operate Software 4.91.00.00

In case of different hard- or software configuration, deviations from the tested functionallity cannot be completly excluded.

Device Settings

Figure 1. S7 Configuration - SINUMERIK

Connection type

The connection type cannot be changed when using the "S7 - SINUMERIK" mode.

IP address

The IP address (or host name) of the CPU. To use a specific port, the port number can be stated with the IP address, e.g. "192.168.1.13:120". The default port for the S7 driver is 102.

Rack

The Rack cannot be changed when using the "S7 - SINUMERIK" mode.

Slot

The slot number of the CPU unit of the PLC. This has to be considered for different PLC assemblies, e.g. S7-300 and S7-400. Please note that WinCC OA stores the slot information as decimal values whereas Step7 and the SIMATIC manager use hexadecimal values.

Timeout [ms]

Defines the timespan for ACCON-AGLink in which all connections must be cleared. If the timespan is exceeded the following error message is displayed:

Asynch. ExitAdapter does not complete for <Connection Name> device <Device Index>

Active

This check box is used in order to set the connection to the peripheral device active or inactive. You can deactivate a connection that is already created and configured. The connection data point is not deleted and can be reactivated at any time. The status display changes from "Connected" to "Not Active"; if a connection is deactivated.

State

Shows the status of the connection to the periphery. The following states are possible:

  • "Not Connected" (Connection to the peripheral device lost e.g. PLC was disconnected from the network)
  • "Connected" (Connected with the peripheral device)
  • "General Query" (General query runs)
  • "Not Active" (Device with the associated check box set to inactive).

GQ

A GQ (General Query) cannot be performed when using the "S7 - SINUMERIK" mode.

Additional Notes

readOpState

In case you are seeing the following error message within the LogViewer, the value for [s7] ReadOpState must be set to 0.