Configuration details
Key Description
- ✔
- Applies to this component
- ❌
- Does not apply to this component
- N/A
- Not Available / Not applicable for this component
Note: Please note that a technical limitation of
the driver connections cannot necessarily be achieved by a single driver. Depending on
the load and dimensioning of the system, number of data transfers, etc., it is
recommended to divide the driver connections among several driver instances or
distributed systems in order to reduce the individual load of a driver.
Driver | Recommended/technical limit of connections per driver | Multiple driver instances | Redundant network | Redundant devices | Special hardware requirements |
---|---|---|---|---|---|
Modbus/TCP Driver | 1000, (Technical limit by Operating System Resources) | ✔ | ✔ | ✔ | Serial/TCP converter for Modbus RTU/ASCII |
Modbus/TCP Server | 100 | ✔ (different port) | N/A | N/A | ❌ |
Ethernet/IP Driver | 100 (Only up-to 8 connections per PLC) | ✔ (different port) | ❌ | ❌ | ❌ |
OPC UA (DA) | 50 (technical limit) | ✔ | ❌ | ✔ | ❌ |
OPC UA (AC) | 50 (technical limit) | ✔ | ❌ | ✔ | ❌ |
OPC UA (HA) | 50 (technical limit) | ✔ | ❌ | ✔ | ❌ |
OPC UA Server (DA) | 50 (technical limit) | ✔ (different port) | N/A | N/A | ❌ |
OPC UA Server (AC) | 50 (technical limit) | ✔ (different port) | N/A | N/A | ❌ |
OPC UA Server (HA) | 50 (technical limit) | ✔ (different port) | N/A | N/A | ❌ |
OPC Client (DA) | 10 | ✔ | ❌ | ❌ | ❌ |
OPC Alarms & Events Client | 10 | ✔ | ❌ | ❌ | ❌ |
OPC HDA Client | 32 | ✔ | ❌ | ❌ | ❌ |
OPC Server | 10 | ✔ (only 2) | N/A | N/A | ❌ |
OPC Alarms & Events Server | 10 | ❌ | N/A | N/A | ❌ |
OPC HDA Server | 10 | ❌ | N/A | N/A | ❌ |
IEC 61850 Driver | 60 with 20 RCBs each (technical limit 200 connections in total) | ✔ | ✔ | ✔ | ❌ |
IEC 60870-5 Driver (101) | Limited by mode (balanced/unbalanced) and hardware configuration (bus, interface) | ✔ | ✔ | ✔ | LAN to Serial converter if no serial interface is available on the PC |
IEC 60870-5 Driver (104) | 1000, (Technical limit by Operating System Resources) | ✔ (different port) | ✔ | ✔ | ❌ |
MQTT | 100 | ✔ | ✔ | ❌ | ❌ |
PROFIsafe Driver (PROFIsafe) | 1 | ❌ | ✔ | ✔ | PROFINET network card of type CP1616 required |
PROFIsafe Driver (PROFInet) | 1 | ❌ | ✔ | ✔ | PROFINET network card of type CP1616 required |
RK512 Driver | 1 | ✔ | ❌ | ❌ | LAN to Serial converter if no serial interface is available on the PC |
S7 Driver | 256 (technical limit; maximum of 512 per project) | ✔ | ✔ | ✔ | ❌ |
S7Plus Driver | 100 | ✔ (The maximum number of instances per host is 30. For further instances another machine must be added.) | ✔ | ✔ | ❌ |
S-Bus Driver | 50 | ✔ | ❌ | ❌ | ❌ |
SNMP | 1000 (Technical limit from resource consumption) | ✔ (different port) | ❌ | ✔ | ❌ |
SNMP (Live Agent) | 100 | ✔ (different port) | ❌ | ❌ | ❌ |
SSI Driver | 100 | ✔ (different port for server mode) | ✔ | ✔ | ❌ |
TLS Gateway | 100 | ✔ (different port for server mode) | ❌ | ❌ | ❌ |
BACnet Driver | 200 | ✔ (different port) | ❌ | ❌ | ❌ |
DNP3 Driver | 100 | ✔ | ❌ | ❌ | ❌ |
SINAUT Driver | 50 | ✔ | ❌ | ❌ | Master TIM |
Cerberus Driver | 1 | ✔ | ❌ | ❌ | MK7022 |